Here are a few ways of adding this option in the controller system:
A controller system with FlexPendant Interface option or any option can be created using System Builder.
If you want to add the option FlexPendant Interface or any other option in an already existing controller system you could do this using System Builder.
But inorder, that the changes be applied to the controller system, an I-start is required.
The error you may be facing can be because of point 2. If yes, have you done an I-Start after modifications to controller system ?
Yes, I have made the same as you adviced, but the problem still persist.
I got a message when I start the TP “Error loading the xxxtpsview.dll” or something
After you have modified an existing system in System Builder and added the FP option, you need to I-start the system for the changes to take effect. Note that this will erase all the RAPID code, and configuration changes in the system.
I successfully installed the FlexPendant Interface in the controller, BUT, when I want to use my project, (some Run routine buttons, only in manual mode) I got this error message:
So, I dont know what is the problem, because in the simulation everything is working, but in REAL system, it doesnt.
Please share your ScreenMaker project and RobotStudio Pack and Go if possible. And also mention which RW version the real system is using. This would help us.