I have four robots. 3 of them require 3x480V and one, an IRB140 says 3x262V, 1x230V. I have hooked up the 140 to 1x230v and the controller comes on and everything looks good until I try and move it. It then says it is missing a phase. Is there a setting that tells the controller to run on single phase?
In addition, I would like to know if anyone has ever used a rotary phase converter or a VFD to get 3 phase from single phase to run a robot? I have the three world transformers, option 930-1. But I would like to get these robots working, but I only have single phase power.
Yes, I see that it is showing a 1600, but it is connected to a 140 and has been running for years on this controller. It does have the world transformer, 930-1.
Update: I purchased a single phase to three phase controller. Mine is single phase 240VAC to three phase 240VAC. I then used the 220VAC tap in the world transformer and everything is working great.