I have a controller configured in IoT Gateway.
It seems all is correct. From an OPC client I can display the tree with the
Objects, types and views, but I do not display any RAPID variables.
Can someone help me ?

Note : Is a virtual controller from RobotStudio
You can only view “Pers” variables. Do you have any of those?
Yes, I have PERS variables.
On the other hand, if I install OPC DA I can see everything

Regards
Make sure you have to correct RobotWare options. You can check in the manual which ones are required for respective RobotWare.