Issue with Profinet configuration

The board is on the slot directly on the main board

I found PROFINET Configurator in an old RW installation backup
PROFINET Configurator seems to allow only Master configuration. My robot needs to be Slave of the PLC.


In the installation is Net+Names : When I connect to the PN Board, I can see the complete PN network.


Please find PROFINET Configurator files here :
https://luxtransfer.lu/fr/download/e49afb80-583d-4b92-b428-cb029d56bf9e#i7Zah1buxZVA-5V7AwOvlc0R_p-AWYZ6bvre3Ul4t3g

Hi. I was out from work yesterday. I got a “file not found” error on that link. Select PCI for the connection instead of LAN. The key should only be to name the station for the robot with NetNames+ and to ensure that the IP address is correct and I think that you should be good from there.

Hi,

Please find a new link : https://luxtransfer.lu/fr/download/5713381e-2e4c-4ec9-85c2-fc81b44998fd#aT8eP-MXF6xlIHTUJf1U4dy7hDKtkE68x_MHEQvwK5c

Hi, that one froze up at 85%.

Did you look at that other software I posted the link for?

I just succeed to run PLCnext Engineer 2025.9, but we didn’t find how to connect to the CP1616 board.

Hello,
Have you made it work yet?

Hi,

not yet, my colleague PLC programmer is on holiday.
The customer wants to test one robot with a fieldbus adapter anybus : DSQC688 and soft option : 840-3 ProfiNet fieldbus Adapter

I revisited the picture you posted, I had to zoom in a lot. There are two ethernet cables plugged into that card, where do they go?

This picture was from some test, there is only one cable to PLC

Oh, OK. Direct to the PLC or is there a switch in between?

There is 2 robots connected to PLC

There is 2 robots connected to PLC

There is 2 robots connected to PLC

OK. So, the profinet gateway address from the last configuration is the IP address of this switch?

Hello,

sorry for the late reply.

The Ip address of the DSQC-678 board is 192.168.10.51

Hello again. Have you added the EIO_UNIT for the IO, PN_INTERNAL_SLAVE Unit Type? And the switch IP address matches the gateway IP address?

We are not able to change the current IP address which is 192.168.1.100.

As I understood we could only make by generating a xdb file with the PLC software, that we didn’t succed until now.

There may be a misunderstanding here. I am not asking you to change the switch IP address, just make the gateway in the EIO.cfg match the switch address.