We would like to connect to S4C+ controler some safety barriers. We are thinking that these barriers could be controled by laser. May be some one where in controller electical circuit we could connect them, that robot motors and welding system could be stopted when someone enter into safety area?
May there is some contacts or IO’s, which we could shorten and stop the system???
I’m thinking to use ABB (AOR500-B75N-T-KK) photoelectric sensors. I think to connect these sensors to panel unit (A81) some there between [X7(10) and X6(15)] or [X7(8) and X6(17)]. Like this, sensor’s output relays should break the chain of emergency stop. Do I think correct?
There are three safety circuits in the S4C+ controller: emergency stop (always active, needs to be resetted with the motors on button on the controller), general stop (always active, no special reset) and auto stop (active in automode only, no special reset). So you can select which one to use.
We connect safety light screens and service doors normally to the autostop, so that these are not active in manual mode, allowing the operator to enter the cell to program.
Hi. Im setting up an old 6400 with s4c+ cabinet. I want to connect a pluto safety plc wich has 2 gates and 2 barriers connected to the auto stop on the robot. I once took an electrical course on theese robots and I have some notes from that event but I dont understand what I have drawn. Maybe I was drunk.