I’ve already read “How to Set Up I/O on a ABB Robot with and IRC5 Controller” but I’m still having troubles after follow the procedure.
DSQC 651 Output1: -1 Input1:-1
NS and MS LEDs are Green
Output V+ and V- are connected to the source.
Mapping is done:
Name: do_1
Type of signal: Digital Output
Assigned to Unit: Discrete651_10
Unit Mapping: 0
Outputs voltage: 1.5V
Inputs Voltage: 0V
I Simulate the signals to 1, and nothing change the voltages are the same.
I changed Output1 and Input1 as EDS file says: Output1:1 and Input1:5 but match a error size.
If someone has this problem with DSQC651, try to use a higher value for Unit Mapping. In my case I solved this using 32 for signal 1, 33 for signal 2, …
Simulating an input will not make the voltage go high on an input, only the real input will. Simulating an output and turning it high will also not make the voltage go high. In fact, it will block the voltage because you simulated it. There is no need to simulate an output, just turn it on. If you still have any simulated outputs, you should remove the simulation.